Stud spacing for 11' exterior walls only supporting roof and ceiling?

Jesse
hace 7 años

I'm getting ready to frame a garage addition on my home, and the architect's drawings call for 2x4 studs at 12" o.c. I second guessed him on this, but he said anything over 10' in height requires this spacing for 2x4s.

So I called the building inspector, who said at 11', I can do 2x4 at 16" o.c.

The plans that were approved for permit say 2x4 at 12" o.c. The architect is backed up on getting some other revisions done, so I haven't been able to re-submit new plans at 16" o.c. yet. The framing starts this week, and I just want to be sure we do it right. I know the building inspector told me it was fine, but I'd feel better if someone else could verify. I've tried looking in the 2015 International Building Code myself, but I can only find the following:

  • 10' maximum height for 2x4 at 24" o.c. (supporting roof and ceiling)
  • 10' maximum height for 2x4 at 16" o.c. (supporting one floor, roof, and ceiling)

My walls are 11' and only support a roof and ceiling.

Thanks for you help!

Comentarios (11)

  • greg_2015
    hace 7 años

    The framing starts this week, and I just want to be sure we do it right.

    Wouldn't the safest bet be to frame it the way the architect said and the plans that were passed show?

    I'm not sure why you'd feel the need to second guess this. It'll only save you a couple of bucks in timber. Or is there some other cost that you'd be saving that I'm not thinking of?

  • just_janni
    hace 7 años

    IMO building strictly to "meet code" is a huge disservice and while you CAN, why WOULD you?

  • User
    hace 7 años
    Última modificación: hace 7 años

    You're looking at the table for 10 ft tall studs. For studs heights above 10 ft, TABLE R602.3.1 limits the height of 2x4's @ 16" o.c. to 12 ft. assuming the following:

    the studs support a roof only; wind speed will not exceed 100 MPH; snow load not exceeding 25 psf; fb not less than 1,310 psi determined by multiplying the AF&PA NDS tabular base design value by the repetitive use factor, and by the size factor for all species except southern pine; E not less than 1.6 × 106 psi, tributary dimensions for floors and roofs not exceeding 6 feet; maximum span for floors and roof not exceeding 12 feet; eaves not over 2 feet in dimension and cover with exterior sheathing.

    Also, Utility, Standard, Stud and No. 3 lumber grades of any species are not permitted for any stud regulated by the table.

    In my experience, it is common to see a poor quality and incorrect grade 2x4s on a job site; it is difficult to monitor the grades unless you are on the site every day; and I would not assume the weather would always cooperate.

    If I were the architect, I would specify 2x6s for an 11 ft wall regardless of the other variables or what the building code says since it would be my stamp on the drawings.

    Jesse agradeció a User
  • Jesse
    Autor original
    hace 7 años
    Thanks for the feedback, everyone. I really don't want to do stud spacing at 12" o.c., so I'll go ahead and frame with 2x6s at 16" o.c. instead.
  • Brian 's
    hace 7 años

    Richard, you are the wealth of knowledge...

  • Jesse
    Autor original
    hace 7 años
    One and a half more questions for you knowledgable, fine folks:

    The bolts have already been set in the foundation for a 2x4 wall. Since I'd like to do a 2x6 wall instead, should I augment them with another fastener into the foundation wall? If so, what do you recommend?
  • User
    hace 7 años
    Última modificación: hace 7 años

    It shouldn't matter unless the inspector objects.

    The greatest talent is knowing where to look.

    Jesse agradeció a User
  • sklka
    hace 7 años

    What is the problem with 12" oc vs 16" oc? A few studs and narrower batts. I would stick with the architects recommendation - tell him you now want 2x6's. Although he may still want 12" oc.


    I had a contractor decide he knew better on a deck - and he changed the angle of the decking material, not realizing that around the corner the new angle would not work. The architect knew.

  • greg_2015
    hace 7 años
    Última modificación: hace 7 años

    I really don't want to do stud spacing at 12" o.c., so I'll go ahead and frame with 2x6s at 16" o.c. instead.

    Okay so it's not a cost savings reason if you're willing to go to 2x6s instead.

    Can you satisfy our curiosity and let us know why you are so opposed to 12" o.c.?

  • User
    hace 7 años
    Última modificación: hace 7 años

    In the 2012 IRC 2x4 studs are limited to 12 ft. at any spacing and 2x6 studs are limited to 16 ft. at any spacing and 18 ft at 16" or smaller spacing..

    This increase in allowable height is because a stud spans vertically from sole plate to top plate and the additional depth of a 2x6 increases the stud's resistance to bending by 250%. (Section Modulus of 2x4 = 3.06 and 2x6 = 7.56).

    The architect is apparently trying to save cost and/or space by decreasing the spacing or he is adjusting for some other condition we are not aware of. But the 2x6's are so much stronger than 2x4's that they can even be installed at 24" o.c.

    The architect has already agreed to the change, he just doesn't have time to change the drawings. I find it odd that this change would require revised drawings. Stud spacings other than 16" o.c. are normally just noted on the floor plan and can easily be changed by a simple written change bulletin from the architect emailed to the owner who could then submit it to the building department.

    Jesse agradeció a User
Patrocinado

Volver a cargar la página para no volver a ver este anuncio en concreto

España
Personalizar mi experiencia con el uso de cookies

Houzz utiliza cookies y tecnologías similares para personalizar mi experiencia, ofrecerme contenido relevante y mejorar los productos y servicios de Houzz. Al hacer clic en 'Aceptar' confirmo que estoy de acuerdo con lo antes expuesto, como se describe con más detalle en la Política de cookies de Houzz. Puedo rechazar las cookies no esenciales haciendo clic en 'Gestionar preferencias'.